Just wondered if 10/3 was sufficient for a 30ft run from a 9500w generator to a 22A air compressor. Or would I need 8/3?

Found someone else who had been there - done that and 10/3 works fine up to around 50ft.
 

bucket

Super Moderator
Staff member
Super Moderator
Joined
Aug 3, 2010
Posts
30,425
Reaction score
28,280
Location
Usually not in Ohio
First Name
Andy
Truck Year
'77, '78, '79, '84, '88
Truck Model
K5 thru K30
Engine Size
350-454
At my old place, I had 10/3 run a distance of around 100ft, from the house to my garage. It worked fine, but I don't know how house current compares to that generator.
 

RustyPile

Left on own accord
Joined
Oct 7, 2017
Posts
901
Reaction score
1,124
Location
Elkhart, TX
First Name
Nick
Truck Year
1983 GMC
Truck Model
1500
Engine Size
350 SBC
The source doesn't play a part in the picture, only the load.. 10-3 is good to 30 amps at 50 feet, dryers, appliances, and some AC systems.. At 22 amps, you're kinda close.. To be safe, I'd suggest 8-3.. YMMV......
 

Ricko1966

Full Access Member
Joined
Apr 11, 2017
Posts
5,405
Reaction score
8,622
Location
kansas
First Name
Rick
Truck Year
1975
Truck Model
c20
Engine Size
350
The source doesn't play a part in the picture, only the load.. 10-3 is good to 30 amps at 50 feet, dryers, appliances, and some AC systems.. At 22 amps, you're kinda close.. To be safe, I'd suggest 8-3.. YMMV......
This,and put an appropriate sized breaker at the end of the run at the compressor.
 

Doppleganger

Full Access Member
Joined
May 24, 2019
Posts
12,680
Reaction score
58,797
Location
OH-MI: Just like it sounds
First Name
Chris
Truck Year
1985
Truck Model
K20
Engine Size
5.7
I know oil cooled compressors have a harder start surge than air cooled in cold weather - my 30gal 2HP oil compressor wont start in anything around 20*. This will be summer so I'm not worried about it.

Called a place that makes extension cords for welders - they said the same thing. 10/3 for 20A at 25-30ft is fine. They usually go 8/3 for anything over 40ft. Compressor has a 25A breaker at the switch.

I think its all good.

Thanks fellas.
 

Doppleganger

Full Access Member
Joined
May 24, 2019
Posts
12,680
Reaction score
58,797
Location
OH-MI: Just like it sounds
First Name
Chris
Truck Year
1985
Truck Model
K20
Engine Size
5.7
fwiw.....original plan was to have a new skirt poured in front of my garage and while things were torn up, run an underground conduit for 220 and a sub panel in the garage - problem solved. The guy doing the concrete is behind til mid-late summer, so this whole generator thing is because I cant wait that long for power in a state that only has 3-4 months of normal weather a year.
 

Doppleganger

Full Access Member
Joined
May 24, 2019
Posts
12,680
Reaction score
58,797
Location
OH-MI: Just like it sounds
First Name
Chris
Truck Year
1985
Truck Model
K20
Engine Size
5.7
DON'T run the compressor until the generator has come up to snuff.
Yep. Generator's owners manual says same thing. When I run the whole house on it. Let it run for about 3-5min, then one flip one breaker at a time. Runs smooth.
 